Following are the more significant parameters:
|
Parameter |
Description |
Default |
|
Current set point |
Current value of the Set Point variable on the rack |
- |
|
Minimum set point |
Minimum value available for the Set Point variable. |
- |
|
Maximum set point |
Maximum value available for the Set Point variable. |
- |
|
Gradient |
It sets how the set point variable value will be increased or decreased following duty cycle calculations on showcases. |
- |
|
Time window for DC calculations |
Indicates how long the data corresponding to the solenoid on each individual showcase is saved in the memory. The duty cycle will be calculated based on these data; once the window is full, each new value will overwrite the oldest value. The value may vary from 10 to 180 minutes. |
12 minutes |
|
DC calculation frequency |
Indicates how often the duty cycle must be calculated for rack showcases and, consequently, the set point changed if necessary. The value may vary from 10 to 180 minutes. |
30 minutes |
|
Maximum failed connection time |
Maximum percentage of failed acquisitions for each showcase associated with the rack If this is exceeded, the showcase is considered offline. |
30% |
|
Maximum number of showcases not connected |
If when the duty cycle is calculated the showcases that are offline exceed this number, the set point is not changed on the rack. |
3 |
Following are the more significant parameters:
|
Parameter |
Description |
Default |
|
Last sample |
Time of the last completed sample. |
- |
|
Current set point |
Current value of the Set Point variable on the rack |
- |
|
Minimum set point |
Minimum value available for the Set Point variable. |
- |
|
Maximum set point |
Maximum value available for the Set Point variable. |
- |
|
Gradient |
Sets how much the set point will be increased or decreased based on the configuration. |
- |
|
Number of set utilities |
Number of showcases linked to the rack. |
- |
|
Number of samples |
Minimum number of samples required to show the showcase and rack status trend. |
3 |
|
Interval between samples |
Time interval between two samples. |
10 minutes |
|
Timeframe |
Minimum time period to show the showcase and rack status trend. |
30 minutes |
|
Yellow |
Number of admitted yellow leds in a sample. |
- |
|
Orange |
Number of admitted orange leds in a sample. |
- |
|
Red |
Number of admitted red leds in a sample. |
- |
|
Led color |
Description of the rack or showcase status |
|
|
Showcase OK. The showcase is correctly operating from the Smooth lines algorithm standpoint: the rack set point can be increased. |
|
|
First warning: the showcase has switched from OK (green led) to NOT OK. |
|
|
Second warning: the showcase remains in NOT OK status for 2 consecutive samples (the led was yellow at the last sample). |
|
|
Third warning: the showcase remains in NOT OK status for 3 consecutive samples (the led was orange at the last sample). |
|
|
Offline: the plug-in cannot read the showcase or rack set point value. |
|
N/A |
The showcase does not support the Smooth lines algorithm: the plug-in cannot read the showcase set point variable value. |
|
|
If N/A status persists for a showcase, it should be eliminated from the group. In fact, the rack is forced to constantly work in safety conditions, at minimum set point, when the Smooth lines algorithm is not supported. |